There are exceptions to this code rule.  Such as where the ground
electrode and conductor are sufficiently sized to handle the calclulated
fault current without excessive voltage drop.

I agree that willy-nilly random bonding of the neutral to ground is a
dangrouse situatuion.  But one which if carefully designed isn't an ONLY
condition.

MM

> From: "Jerry Mathis" <thebeaver32 at gmail.com>
>
>> A situation with the neutral bonded to ground anywhere outside the
> distribution panel or service entrance is a serious problem.
>
> Neutral and safety ground should never be tied together EXCEPT at the
> SERVICE panel
>
> Tying them together anywhere else (sub-panel) is a violation of the NEC
>
> That is NOT to say you can't have a second ground rod
> elsewhere.............say at a garage detached from the house that is 'old
> wiring' with no separate ground wire going back to the entrance