[BC] LAN Weirdness
Gary Glaenzer
glaenzer at verizon.net
Sat Feb 13 12:14:12 CST 2010
From: "Jerry Mathis" <thebeaver32 at gmail.com>
> A situation with the neutral bonded to ground anywhere outside the
distribution panel or service entrance is a serious problem.
Neutral and safety ground should never be tied together EXCEPT at the
SERVICE panel
Tying them together anywhere else (sub-panel) is a violation of the NEC
That is NOT to say you can't have a second ground rod
elsewhere.............say at a garage detached from the house that is 'old
wiring' with no separate ground wire going back to the entrance
More information about the Broadcast