[BC] CONTINENTAL 315R-1 5KW AM TROUBLE
Tom
Radiofreetom at gmail.com
Sun Oct 28 19:27:25 CDT 2007
And someone else mentioned no drive... I imagine you checked THAT, though...
BTW - where did you find rack adapters for your head? Mine's nowhere
NEAR 19".... :-P
Tom S.
Tom wrote:
> First clue is the HV input reading - pegged meters. Make sure they're
> really seeing that much (HV probe time!), and it's not a shorted
> multiplier resistor; then check backwards from that. Possible causes
> - open filter cap(s) in the power supply allowing excessive ripple,
> problems with the transformer (not fully familiar with this PS, but
> many transformers can be tapped / connected for various secondary
> values allowing different transmitters to use same PS - and
> up-powering any given box easier as a side benefit. If there's a
> lower value available, you might be able to connect the lower voltage
> to at least get the rig back on the air. The cure will be, in that
> case, a new transformer.
> Also check - three-phase? - AC incoming; a floating phase might be
> giving you more voltage in one leg than you're supposed to have.
> Might be power pole pig, might be neutral, but if the incoming's not
> right, you can get all SORTS of problems. Had one back when I was
> just starting out as an engineer - might have been a Continental, it's
> been a while - that the power company provided three-phase with
> what's called a "wild phase"; the reactance of the transformers
> generate the third leg "virtually". We kept popping rectifier stacks,
> and nothing would help - MOVs, bypass caps, you name it. Finally we
> checked phase-to-phase and phase-to-neutral, both with and without the
> transmitter on. BIG difference! I left shortly after that; not sure
> who wound up paying for getting true three-phase service out there...
> or if they did, even.
>
> HTH
>
> Tom S.
>
> BOYDSIRBOYD at aol.com wrote: SNIPPED -
More information about the Broadcast