[BC] Humming Preamps
Mike Holderfield
mikeholderfield
Sun Apr 8 00:57:20 CDT 2007
If it is intermittent and in a multi-story building don't
forget the elevator service. I've heard it happen.
Every time they moved, a buzz & weird harmonic sound.
mike
Gary Peterson wrote:
> I've seen two situations where hum or buzz got into radio station audio
> equipment via the power line. The first time, it was a water heater that
> was defective. Every time the heating element came on, hum appeared in
> several pieces of audio gear. Some were tube and some were solid-state.
> This was circa 1968. It was located by flipping breakers in each panel in
> the building until the hum quit. A replacement water heater solved that
> problem. I guessed that there was leakage between the 240 VAC in the
> heating element to the plumbing and electrical ground.
>
> At another site, circa 1985, a buzz appeared, from time to time, in the
> preamps on the Carousels in the automation system. This was traced to some
> recently installed track lighting, with a SCR dimmer, in another office in
> the building. All attempts at filtering out the noise, at the source,
> failed. We finally bought them a Variac-type of dimmer.
>
> If you can do it, start shutting down various circuits and see what happens.
> A couple of FRS handheld radios would come in handy.
>
> Gary, K?CX