Barry Mishkind wrote:
> At 11:26 AM 7/3/2009, Chris Gebhardt wrote:
>> Also, as provided in our DR plan, if our generator fails, we have a
>> standing reservation to have a rental unit rolled up. Response time on
>> that is 4 hours. (Also, if we are on generator for >4 hours, we put a
>> spare on standby.)
>
> Chris, out of curiosity, how long does your UPS last in the
> event both power feeds die?
Not long! We have about 30 minutes worth of UPS with our current
battery string. We could extend that by adding battery of course, but
the design of the system is that if both electric services fail,
generator takes over. Our generator will assume the load within 30
seconds (including bounce delay). If our utility feeds AND generator
both fail, we wait on a replacement generator. In most cases that will
arrive within 2 hours, but guaranteed 4.
But keep in mind that it would be exceedingly difficult to put the CRACs
(computer room air conditioners), chillers and glycol pumps on battery
and have them last for very long. So the longer the datacenter runs on
battery alone, the warmer it gets.
We have the generator professionally maintained, exercise it weekly and
transfer load monthly. We do our best to ensure that even if the
utility falls down, we do not.