[BC] More thoughts about AM transmitter lightning sensitivity issue
Mike McCarthy
Towers at mre.com
Wed May 21 22:20:30 CDT 2008
You have received some sage advise. I have a site with a reset macro
written to allow two resets in a 10 minute period. If more than two
occur, it requires a manual reset. I have found that usually two
resets won't damage a TX and keeps nuisance calls to a minimum. If
the fault is that severe, the TX will self protect and survive the
lone remaining reset. The problems occur when the TX's fault
protection circuits are disabled and no reset limit employed.
I concur with checking the ball gaps and setting them to the point
where they don't arc with peak modulation, plus 1/8". If the towers
are low impedance, you can get the balls to within 1/8" and still run
3+ KW. That should calm down the trips significantly in all but the
most intense part of the storm.
I would however have the lightning protection aspect of the ground
system checked by a consultant specializing in ground systems. While
you might have the greatest RF ground system, the deeper electrodes
and associated components driven in 1947 might have issues with
accumulated electroplating or marginal mechanical connections
limiting the effectiveness of the overall dissipation network. I
have seen sites where ground rods had eroded in a similar manner to
guy line anchors eroding due to electrolysis. Those sites were all
built pre-1960 in good soil and the surface appearance was noted as
normal/nominal.
Additionally, very old electrodes can also be sitting within a column
of insulating materials from years of current conduction turning the
soil into something other than soil. I recall a story from a phone
CO which started having increased reports of damage from storms and
unexplainable issues with hum, DC offset, and a plethora of other
phenomena. They unearthed the ground system and found it surrounded
by 6" of crystalline powder. All the current flow from the CO
altered the PH of the soil so much that there wasn't anything left to
give and the ground simply crystallized towards a sand
composition. The same was true of the electrical service ground as
well. They replaced the system and all was well again.
MM