[BC] Comparing the audio in the Big 50's
Robert Meuser
robertm at nyc.rr.com
Wed Jun 20 08:31:55 CDT 2012
For older stations this should not be a big problem since the older
transmitters required so much more power so there would already a lot of
power available. Remember a few stations had their own substations
taking only an HV feed from the utility.
When building a new station it gets trickier as many utilities will try
to undersize the feed. The best way to assure adequate power is to over
state the load. The first thing is assume that if a station has 2 50 KW
TXs they will both be on even if one is only tested on the generator.
While it costs money, renting a load bank (which may be necessary for
generator testing anyway) and kicking up the peak demand in the
beginning will justify any over estimating and keep the power company
happy. Once the service is in, they will not come back and downgrade.
Today it is a moot point with the latest solid state transmitters that
have multiple single phase power supplies distributed across the three
phases. There is enough capacitance to support modulation peaks.
On 6/20/12 8:00 AM, Dave Dunsmoor wrote:
> Makes me wonder, how much of the various 50kw stories regarding
> "sounds good" vs "not so much" and the 100kw power supplies, etc might
> be attributable to the "stiffness" of the utility power at the
> facility itself?
>
> Pulling 100kw of clean power off the grid *should* be somewhat related
> to the internal impedance of the AC supply (transmission lines,
> substations, generators, etc) but is this much of a practical concern?
>
More information about the Broadcast
mailing list