[BC] 110 V DC
PeterH5322
peterh5322
Sat Dec 2 17:02:38 CST 2006
>I was questioning if the voltages that Peter quoted corresponded to our
>120-208 and 277-480 systems
North America is predominately a 120/240 single-phase system, which is
inherently 240 three-phase delta.
EU (and others) is predominately a 220/230/340 system, which is
inherently wye.
In North America, you get three wires: 120 volts to ground, neutral, and
120 volts to ground.
240 is obtained from the two ungrounded conductors.
120 is obtained from either of the two ungrounded conductors to the
neutral.
Three-phase 240 delta is possible, as is three-phase 480 delta.
Most three-phase, however, is 120/208 wye, or 277/480 wye.
(Almost all transmission is delta, as this requires only three
conductors, and has no "zero sequence" currents. Wye transmission, which
requires four conductors, and has "zero sequence" currents, is rare).
In Europe (and elsewhere) there is one ungrounded conductor and one
grounded conductor.
The ungrounded single-phase conductor could be 220, 230 or 240,
corresponding to a 380 wye, 400 wye or 415 wye three-phase system.