On Jun 29, 2009, at 4:13 AM, RichardBJohnson at comcast.net wrote:
> Delta is nice because it provides good balance. However, you need
> to use a transformer to generate 120/240, which puts your entire LV
> panel on one incoming leg.
The most popular form of Æ is 120/240.
If a three-phase transformer is installed, the capacity of the A-C
phase, which is that which supplies 120/240 loads, and the capacities
of the A-B and B-C phases, which are those which supply only three-
phase loads (or customer-installed and owned "dry-type" single-phase
distribution transformers) are the same.
In the more usual case, a larger singe-phase transformer will be
installed for the A-C phases, and one smaller transformers will be
installed for the A-B phases, or two smaller transformers will be
installed for the A-B and B-C phases. The former is called "open Æ",
the latter is called "closed Æ".
Let's say your installed three-phase load is 50 KVA, and your
installed single-phase loads are 100 KVA.
This could be accommodated by a 150 KVA 120/240 transformer plus two
50 KVA 240 transformers.
One advantage of Æ is there can be no "zero-sequence" currents in an
ungrounded system. There will always be "zero-sequence" currents in a
Y system.
Æ is used for most transmission and subtransmission systems as Æ
requires only three conductors (Y requires four conductors), plus Æ
can still deliver three-phase power in the presence of a temporary
single line-to-ground fault (any line-to-ground fault in a Y system
results in loss of power).
Y is occasionally seen in older subtransmission systems where the
original Æ system was "Y-ed up" to a higher subtransmission voltage.
The required insulators are the same, so a Æ may be converted to a Y
simply by adding a fourth conductor, which is a neutral conductor,
and which is normally at ground potential, but carries any "zero-
sequence" currents (currents attributable to an imbalance in the
three phases).
A 7,200 volt Æ system may, thereby, be converted into a 12.5 kV Y
system quite economically, as the line-to-ground voltage in both
cases is 7,200 volts..